T320 Honeywell Server Planning, Installation and Service Guide HWDOC-X239-en-I August 2020...
Page 2
Honeywell International Sàrl. While this information is presented in good faith and believed to be accurate, Honeywell disclaims the implied warranties of merchantability and fitness for a purpose and makes no express warranties except as may be stated in its written agreement with and for its customer.
2.1.1 Software requirement 2.1.2 BIOS configuration 2.2 Description 2.2.1 Honeywell server model number 2.2.2 Electronics configuration 2.2.3 Electronics module 2.2.4 Standard features of Dell T320 2.2.5 Slots configuration 2.2.6 Optional features 2.2.7 Power cords 2.3 Platform information 2.3.1 Honeywell documentation 2.3.2 Dell documentation...
Page 4
3.2.1 Grounding consoles and cabinets 3.3 Cabinet spacing requirements 3.3.1 Unused cabinet spaces 3.4 Installing Dell T320 server and connecting cables 3.4.1 Honeywell server back panel connections 3.4.2 Installing the server using the fixed rail mounting kit model TP-SPCMF1 3.4.3 Installing the server using the slide tray mounting kit model TP-SPCMS1 3.4.4 Connecting the cables...
Page 5
5.6.2 To add additional memory 5.7 Installing hot spare hard drive 5.7.1 To insert the hot spare hard drive 5.8 Installing PCIC card in Dell T320 server using Magma 5.8.1 To insert the Magma PCIe card 5.9 Verifying correct BIOS settings 5.9.1 Entering the BIOS...
Page 6
5.9.2 BIOS settings for Tab 51155517-100 5.9.3 BIOS settings for Tab 51155517-200 5.9.4 BIOS settings for Tab 51155517-300 5.9.5 BIOS settings for Tab 51155517-400 5.9.6 BIOS settings for Tab 51155517-500 5.9.7 BIOS settings for Tab 51155517-600 5.9.8 Exiting the BIOS 5.10 Spare parts 5.11 Troubleshooting 5.11.1 Integrated Dell Remote Access Controller 6 (iDRAC6) issue...
BOUT THIS OCUMENT This document contains installation and service information for the Dell PowerEdge T320 server. The instructions and service information contained here address the server itself, and assumes that the associated network communication equipment has been pre-installed by the Honeywell factory or has manuals dedicated to its installation and service.
Page 8
Chapter 1 - About this Document Publication Content Type (EPDOC-X478-en-511A) Experion LCN Planning, ELCN system planning, hardware/software Installation, and Service Guide installation, servicing/troubleshooting (HWDOC-X479-en-E) Experion LCN Specification General ELCN technical specifications (ELCN03) Fault Tolerant Ethernet FTE system installation, servicing/troubleshooting Installation and Service Guide (EPDOC-XX36-en511A) Universal Embedded General UEA planning, installation, and service...
Chapter 1 - About this Document Publication Content Type Experion Network Best Best practices for planning the installation of Experion Practices (WP-07-02-ENG) FTE networks, and connecting them into plant IT networks. Experion R511 Software Describes Experion R511 features/enhancements, Change Notice (EPDOC- overall product, release interoperabilities, system X166-en-511A) dependencies, problem resolutions, known issues,...
Use of any other server including a similar Dell model, is considered a project special and its TAC support is limited according to the services policy. The Dell PowerEdge T320 server are shipped with the following Tab numbers. The CPU and memory configurations varies for each Tab number.
The BIOS version for the server depends on the Tab numbers. The Tab numbers for Dell PowerEdge T320 server are: 51155517-100: with BIOS version 1.3.5 [Honeywell 1.0.0] 51155517-200: with BIOS version 1.3.5 [Honeywell 1.0.0] 51155517-300: with BIOS version 1.3.5 [Honeywell 1.0.0] 51155517-400: with BIOS version 2.0.22 or later...
Windows Server 2016 standard COA COAS16 2.2.2 Electronics configuration The Dell T320-based server is approved for installation in 800 and 1000 mm deep Honeywell LCN cabinets using either a "fixed" mounting kit, model number TP-SPCMF1, or a "slide" mounting kit, model number TP-SPCMS1. 2.2.3...
Platform information Honeywell documentation Dell documentation 2.3.1 Honeywell documentation The following table lists the Honeywell publications that may be useful when installing or operating your system. Publication Contains information about Fault Tolerant Ethernet Installation and Installing and using FTE on a TPS or Service Guide Experion PKS node.
Page 16
Packaged with Guide system. the computer Product Documentation Dell™ PowerEdge™ Removing and replacing the parts. Technical Product T320 Systems specifications. Configuring the system. Documentation Hardware Owner’s Troubleshooting. Manual www.dell.com Rack Installation Installing the server in a server rack or Packaged with Instructions —...
Chapter 2 - Planning LCN node slot requirements Slot number Description Option Slot 1 PCIe_G2x4 Slot 2 PCIe_G2x1 Slot 3 PCIe_G3 x16 _CPU1 LCNP4e/LCNP4e2 Slot 4 PCIe_G3x4_CPU1 Slot 5 PCIe_G3x16_CPU2 Not Populated Slot 6 PCIe_G3x4_CPU1 Empty for MZ-PCSV71 PERC H310 Controller for MZ-PCSV72 PERC H710 Controller for MZ-PCSV73 NOTE A Local Control Network Processor (LCNP) board and LCN Media Access Unit (MAU) are no...
Memory configuration for Dell T320 Standard memory for all the three variants of Dell T320 MLK server is 8GB (2x4GB) RDIMM, 1333MHz or faster and it must be installed in pairs. The label on the outside of the shipping container shall identify the capacity of the memory installed.
Chapter 2 - Planning DIMM socket Memory size Total memory Not available for use Not available for use 2.6.3 8GB, consisting of two 4GB RIDMM for MLK servers The following table provides memory configurations layout for 8GB, consisting of two 4GB RIDMM for MLK servers.
Page 23
Chapter 2 - Planning temperature gradation of 10° per hour . Note : for Altitudes above 2950 feet , the maximum operating temperature is derated 1 °F/550 ft. All temperature ratings shown are for sea level. An altitude derating of 1 °C per 300 m (1.8 °F per 1,000 ft) to 3048 m (10,000 ft) is applicable.
Chapter 2 - Planning NH3 Gas concentration NH3 Gas concentration < 2 mm3/m3 parts per billion O3 Gas concentration G1 mild environment limits as per ANSI/ISA-S71.04- Severity level 1985 Standard ANSI/ISA-S71.01-1985 Temperature and Humidity Environmental Conditions for Process Measurement and Control Systems ANSI/ISA-S71.04-1985 Airborne Contaminants...
Chapter 2 - Planning 2.7.13 Altitude Operating -15.2 to 3048 m (-50 to 10,000 ft) Note: For altitudes above 2950 feet (899.16 meters), the maximum operating temperature is derated 1 °F/550 ft. (that is, 1 °F /167.64 m that is,-17.22 °c/167.64 m) Storage -15.2 to 12,000 m (-50 to 39,370 ft) 2.7.14...
PRM SATA 3.5" HDD with hot swap bay. For MZ-PCSV73, the Honeywell-based Dell T320 has four hard disk drive bays. It uses four 146 GB 2.5” or 300 GB 3.5” SAS hard drives for RAID-5 (distributed parity). A 5th 146 GB 2.5” 15K RPM SAS HDD hot spare is available and must be bought separately (P/N MZ-PCEH03).
The Honeywell-based Dell T320 server supports industrial standard video format (typically 1024X768 at a refresh rate of 75Hz). You must use a multisync monitor along with the Dell T320 server platform operating system. The server can be configured only with a single screen option. In this configuration, the monitor is connected to the AGP video controller output connector.
The compliance specifications in this section apply to installations other than cabinets. ATTENTION Honeywell does not claim Safety Compliance or Electromagnetic Compatibility (EMC) Compliance for system equipment configurations that have not been described in this guide as standard system configurations. Any equipment configuration other than that described in this publication decertifies the Safety and EMC compliance of this product.
Chapter 2 - Planning Regulatory) for European community. Element Description Emissions IEC 61326, 1997 (Basic Requirements, CISPR 11, Class A) Immunity IEC 61326, 1997 (Basic Requirements) ATTENTION The following formula is a proximity guideline, for use of Portable Transceivers (walkie-talkies) in the frequency range of 80MHz to 1GHz.
Honeywell cabinet. Tasks for installing the server Power and grounding requirements Cabinet spacing requirements Installing Dell T320 server and connecting cables Starting the server Tasks for installing the server The following table lists the major platform installation tasks. Checklist Tasks Understanding the Power and grounding requirements.
Uninterruptible Power Source (UPS). Cabinet spacing requirements Due to thermal constraints, only one Dell T320 can be mounted on a new build 1-meter deep Honeywell MP-C1MCB1 cabinet. The server must be mounted on rack space interval 11U through 15U counting from the bottom of the cabinet and moving up.
(mm) deep LCN cabinets, model number MP-C8LCB1-Tab and MP-C1MCB1-Tab respectively. This procedure assumes that a new 800 or 1000 mm deep cabinet was shipped from the Honeywell factory with either the “fixed rail” mounting kit, model number TP-SPCMF1, or the “slide tray” mounting kit, model number TP-SPCMS1, pre-installed.
Page 33
Chapter 3 - Installation NOTE The photo shows the MAU connector attached to the server back panel. The LCN MAU is not used when the LCN is integrated with an ELCN. - 33 -...
Chapter 3 - Installation 3.4.2 Installing the server using the fixed rail mounting kit model TP- SPCMF1 This procedure is the same regardless of whether the cabinet is 800 or 1000 mm deep. Do NOT remove the plastic feet from the bottom of the server (when oriented as a tower). This installation procedure intentionally omits use of the server front bezel cover.
8. If you are using the 8-port KVM switch/control console for your human interface (pre-installed in the Honeywell factory), connect the KVM cable mouse and keyboard connections to the USB connectors on the rear of the server. The KVM cable may have separate USB connections for the mouse and keyboard or they may be combined into one USB connector through a USB to PS/2 adapter (included with the KVM cable).
Page 36
Chapter 3 - Installation 4. The rear retaining bracket is located in a slot in the rear of the slide tray. Position the front surface of the rear retaining bracket approximately 73 mm[2.9 inches] forward of the rear surface of the slide tray.
Chapter 3 - Installation 7. Install the two front retainer brackets. a. Loosen the vinyl cap covered stop pegs and slide them to the outer end of their adjustment slots. b. Engage and tighten the two captivated panel fasteners in each front retainer bracket into the threaded standoffs protruding from the side brackets.
Failure to do so may result in tripping the circuit breakers. 2. Connect the Honeywell AC power cords. 3. Perform any one of the following, as necessary. If you are not using Fault Tolerant Ethernet (FTE), connect the Ethernet cable to the on-board RJ-45 connector.
Page 39
Chapter 3 - Installation To install air duct baffles and blank panel front covers in cabinet 1. Place the air duct baffle inside the cabinet with the bent tab resting along the front of the right cabinet rail. Figure 3.2 Installation of Air Duct Baffle and Blank Panel Front Cover - 39 -...
1. Press the power button on the front panel of the server. 2. Wait for the power light to become solid green. ATTENTION If the power light does not become solid green, refer to the Troubleshooting section in the Dell™ PowerEdge™ T320 Systems Owner’s Manual. - 40 -...
LCNP4e/LCNP4e2 passed self test. To check the LCNP4e/LCNP4e2 status 1. Choose Start > Programs > Honeywell TPS > LCNP Status. 2. Verify that the LCNP status indicates Passed Self Test and the circle is green. 3. Verify that the TPN Address appears in the LEDs field of the LCNP Status display, after the Board 0 is configured for the node’s TPN address.
These servers are provided with 2.5 inch Hot-swappable hard-drive chassis. Figure 4.1 Front panel with 2.5 inch Hot-swappable hard-drive chassis The following image illustrates the front view of the Dell T320 server for MZ-PCSV71. This server is provided with 3.5 inch Hot-swappable hard-drive chassis.
6. System identification button 7. LCD menu buttons 8. Information tag 9. LCD panel 10. USB connectors (2) 11. Hard drives 4.1.2 Rear view of Dell T320 The following image illustrates the rear view of the Dell T320 server. - 44 -...
10. Serial connector 11. External cooling fan power cable slot Network connections Each Honeywell-configured platform must be connected to an ETHERNET network. NOTE A Local Control Network Processor (LCNP) board and LCN Media Access Unit (MAU) are no longer used if the Server has been upgraded to be an ELCN node.
The Honeywell server platform uses only a digital system clock. When the Dell T320 platform is added to an existing system that contains nodes running analog clocks that system must have at least two (2) KxLCN boards for analog/digital clock translation. The model number for the LCNP4e/LCNP4e2 is TP-LCNP04.
Tap Dummy Load (TDL) which terminate a drop cable when no node is present. The model number for the ControlNet Universal Interface is TC-PCIC02-100. The following image displays the PCIC card used by Honeywell. TC-PCIC02: This is a universal PCIC card. - 47 -...
Chapter 4 - Operation ATTENTION TC-PCIC02: Controlnet Network interface can be connected to Dell PowerEdge T320 server using Magma PCIe to PCI converter. For more information on “How to connect using Magma Converter”, refer to the Magma PE3R Installation Instructions available at the following Honeywell Process Solutions support website.
Servicing the LCNP4e/LCNP4e2 Servicing the hard disk drives and power supply Servicing Honeywell options Adding additional memory Installing hot spare hard drive Installing PCIC card in Dell T320 server using Magma Verifying correct BIOS settings Spare parts Troubleshooting Removing the front bezel 5.1.1...
Chapter 5 - Servicing Removing the side cover To remove or installs the components on the motherboard; you must first remove the side cover. 5.2.1 To remove the side cover 1. Press the release latch and lift it up, as illustrated in the following. 2.
Chapter 5 - Servicing Servicing the LCNP4e/LCNP4e2 The LCNP4e/LCNP4e2 board has 256 MB of on-board memory. NOTE A Local Control Network Processor (LCNP) board and LCN Media Access Unit (MAU) are no longer used if the Server has been upgraded to be an ELCN node. Replacing the LCNP4e/LCNP4e2 board 5.3.1 Replacing the LCNP4e/LCNP4e2 board...
Page 52
Chapter 5 - Servicing 6. Press the card retainers (blue plastic notch) and push it back. 7. Remove the metal shield adjacent to the LCNP4e/LCNP4e2 card in PCIe slot 3. - 52 -...
Servicing the hard disk drives and power supply The server from Honeywell is configured with five 146 GB or 300 GB SAS hard drives for RAID-5 configuration and the fifth hard drive is a hot spare. The configuration also contains redundant power supplies.
Getting Help Jumpers, Switches, and Connectors I/O Ports and Connectors Abbreviations and Acronyms Servicing Honeywell options CAUTION Do not damage the EMI gasket fingers when removing/installing boards. WARNING Use a grounding strap and grounded work surfaces and equipment when handling any electro statically sensitive components such as the video cards, NIC adapter cards, and SCSI controller cards.
Server has been upgraded to be an ELCN node. 5.5.2 Slot requirements for General Ethernet and FTE node setup The following table identifies the specific slots for each of the Honeywell options for general Ethernet and FTE node configurations. PCIE-...
The standard memory capacity is 4 GB. The system memory can be increased to 8 GB, MZ-PCEM15. Memory devices must be from the same memory supplier. For further information about the memory configurations, refer to the section Memory configuration for Dell T320. 5.6.1 Prerequisites Turn off the system Disconnecting power cords and cables from the server.
Page 57
Chapter 5 - Servicing 4. The DIMM memory sockets are now exposed. 5. While wearing a grounded ESD wrist strap, press the socket ejectors on the memory module socket down to allow the memory module to be inserted into the socket. 6.
The hot spare hard drive is installed in the server. NOTE In Dell PowerEdge T320 Performance server Server 146 GB Hard disk drives (MZ- PCEH02) are obsolete and Customer may receive Replacement as 300 GB (MZ- PCEH07) Hard disk drives. These drives can be used in RAID5 array with 146 GB Hard disk drives.
Page 59
Chapter 5 - Servicing 6. Press the card retainers (blue plastic notch) and push it back. 7. Remove the metal shield in slot 3. - 59 -...
12. Replace the side cover and the front bezel. Verifying correct BIOS settings All Honeywell systems must have the Honeywell recommended BIOS version. Honeywell configures specific BIOS settings in the factory for each of the server platform configurations, and these settings must not be altered.
2. Press F2 on the keyboard to enter the BIOS Setup. 3. Verify that the BIOS version. 5.9.2 BIOS settings for Tab 51155517-100 System information Product name Dell PowerEdge T320 server System model name T320, 001 BIOS Version 1.3.5 [Honeywell 1.0.0] System manufacturer...
Page 62
Chapter 5 - Servicing Memory information System memory size 4.0GB or 8GB System memory type ECC DDR3 System memory speed 1067MHz System memory voltage 1.35 V Video memory 16 MB System memory testing Disabled Memory operating mode Advanced ECC Mode Node interleaving Disabled CPU information...
Page 63
Chapter 5 - Servicing Processor 1 Family – Model – Stepping 06-0D-7 Brand Intel® Xeon® CPU E5 2403 @ 1.8 GHz Level 2 Cache 4 X 256 KB Level 3 Cache 10 MB Number of cores SATA settings Embedded SATA ATA Mode PORT A / B / C / D Auto...
Page 64
Chapter 5 - Servicing 1. Hard drive C 2. Embedded SATA Port Optical Drive E 3. Embedded NIC Hard disk drive sequence RAID Controller in Slot 6 NA One time boot Column 1 heading Column 2 heading One time Boot Device List Disabled BIOS Boot Sequence Device Hard drive C:...
Page 65
Chapter 5 - Servicing Serial communication Serial communication On without Console Redirection Serial Port Address Serial Device 1 = COM1 Serial Device 2 = COM2 External Serial Connector Serial Device 1 Fail Safe Baud Rate 115200 Remote Terminal Type VT100/VT220 Redirection After Boot Enabled System profile settings...
Network Speed 100 Mbps Duplex Mode Full Duplex 5.9.3 BIOS settings for Tab 51155517-200 System information Product name Dell PowerEdge T320 server System model name T320, 001 BIOS Version 1.3.5 [Honeywell 1.0.0] System manufacturer Dell System Manufacturer Contact info www.dell.com...
Page 67
Chapter 5 - Servicing Memory information System memory size 4.0GB or 8GB System memory type ECC DDR3 System memory speed 1067MHz System memory voltage 1.35 V Video memory 16 MB System memory testing Disabled Memory operating mode Advanced ECC Mode Node interleaving Disabled CPU information...
Page 68
Chapter 5 - Servicing Processor 1 Family – Model – Stepping (06-2D-7) Brand Intel® Xeon® CPU E5 2403 @ 1.8 GHz Level 2 Cache 4X 256 KB Level 3 Cache 15 MB Number of cores SATA settings Embedded SATA ATA Mode PORT A / B / C / D Auto Model...
Page 69
Chapter 5 - Servicing 1. Hard drive C 2. Embedded SATA Port Optical Drive E 3. Embedded NIC Hard disk drive sequence RAID Controller in Slot 6 PERC H310 Adapter One time boot Column 1 heading Column 2 heading One time Boot Device List Disabled BIOS Boot Sequence Device Hard drive C:...
Page 70
Chapter 5 - Servicing Serial communication Serial communication On without Console Redirection Serial Port Address Serial Device 1 = COM1 Serial Device 2 = COM2 External Serial Connector Serial Device 1 Fail Safe Baud Rate 115200 Remote Terminal Type VT100/VT220 Redirection After Boot Enabled System profile settings...
Network Speed 100 Mbps Duplex Mode Full Duplex 5.9.4 BIOS settings for Tab 51155517-300 System information Product name Dell PowerEdge T320 server System model name T320, 001 BIOS Version (1.3.5 [Honeywell 1.0.0]) System manufacturer Dell System Manufacturer Contact info www.dell.com...
Page 72
Chapter 5 - Servicing Memory information System memory size 4.0GB or 8GB System memory type ECC DDR3 System memory speed 1333 MHz or greater System memory voltage 1.35 V Video memory 16 MB System memory testing Disabled Memory operating mode Advanced ECC Mode Node interleaving Disabled...
Page 73
Chapter 5 - Servicing Processor 1 Family – Model – Stepping (06-2D-7) Brand Intel® Xeon® CPU E5 2430v2@ 2.20GHz Level 2 Cache 6 X 256 KB Level 3 Cache 15 MB Number of cores SATA settings Embedded SATA ATA Mode PORT A / B / C / D Auto Model...
Page 74
Chapter 5 - Servicing 1. Hard drive C 2. Embedded SATA Port Optical Drive E 3. Embedded NIC Hard disk drive sequence RAID Controller in Slot 6 PERC H710 Adapter One time boot Column 1 heading Column 2 heading One time Boot Device List Disabled BIOS Boot Sequence Device Hard drive C:...
Page 75
Chapter 5 - Servicing Serial communication Serial communication On without Console Redirection Serial Port Address Serial Device 1 = COM1 Serial Device 2 = COM2 External Serial Connector Serial Device 1 Fail Safe Baud Rate 115200 Remote Terminal Type VT100/VT220 Redirection After Boot Enabled System profile settings...
Network Speed 100 Mbps Duplex Mode Full Duplex 5.9.5 BIOS settings for Tab 51155517-400 System information Product name Dell PowerEdge T320 server System model name T320, 001 BIOS Version 2.0.22 or later System manufacturer Dell System Manufacturer Contact info www.dell.com...
Page 77
Chapter 5 - Servicing Memory information System memory size System memory type ECC DDR3 System memory speed 1333MHz System memory voltage 1.35 V Video memory 16 MB System memory testing Disabled Memory operating mode Advanced ECC Mode Node interleaving Disabled CPU information Alternate RTID Disabled...
Page 78
Chapter 5 - Servicing Processor 1 Family – Model – Stepping 06-3E-4 Brand Intel® Xeon® CPU E5 2403V2 @ 1.80 GHz Level 2 Cache 4 X 256 KB Level 3 Cache 10 MB Number of cores SATA settings Embedded SATA ATA Mode or AHCI Mode ATTENTION During the Init Media installation, if the...
Page 79
Chapter 5 - Servicing Boot settings Boot Mode BIOS Boot Sequence Retry Disabled Boot sequence 1. Embedded SATA Port Optical Drive E 2. Hard Drive C: 3. Embedded NIC | Port 1 | Partition 1 | Partition 1 : BRCM MBA Slot 0100 V15.2.10 Boot option Enable / Disable 1.
Page 80
Chapter 5 - Servicing Integrated devices User Accessible USB Ports All Ports On Internal USB Port Embedded NIC1 and NIC2 Enabled OS Watchdog Timer Disabled I/O AT DMA Engine Disabled Embedded Video Controller Enabled SR-10V Globe Engine Disabled Memory mapped I/O above 4GB settings Disabled Slot Displacement Slot 1 to Slot 6...
Page 81
Chapter 5 - Servicing Serial communication Serial communication On without Console Redirection Serial Port Address Serial Device 1 = COM1 Serial Device 2 = COM2 External Serial Connector Serial Device 1 Fail Safe Baud Rate 115200 Remote Terminal Type VT100/VT220 Redirection After Boot Enabled System Profile...
Page 82
Chapter 5 - Servicing System security Intel AES-NI Enabled System Password Not Enabled Setup Password Not Enabled Password Status Unlocked TPM Security TPM Activation No Change TPM Clear Intel TXT Power Button Enabled NMI Button Disable AC Power Recovery Miscellaneous settings System Time System date Asset Tag...
Network Speed 100 Mbps Duplex Mode Full Duplex 5.9.6 BIOS settings for Tab 51155517-500 System information Product name Dell PowerEdge T320 server System model name T320, 001 BIOS Version 2.0.22 or later System manufacturer Dell System Manufacturer Contact info www.dell.com...
Page 84
Chapter 5 - Servicing Memory information System memory size System memory type ECC DDR3 System memory speed 1333 MHz or greater System memory voltage 1.35 V Video memory 16 MB System memory testing Disabled Memory operating mode Advanced ECC Mode Node interleaving Disabled CPU information...
Page 85
Chapter 5 - Servicing Processor 1 Family – Model – Stepping (06-2D-7) Brand Intel® Xeon® CPU E5 2403V2 @ 1.80 GHz Level 2 Cache 4 X 256 KB Level 3 Cache 10 MB Number of cores SATA settings Embedded SATA ATA Mode or AHCI Mode ATTENTION During the Init Media installation, if the...
Page 86
Chapter 5 - Servicing 1. Embedded SATA Port Optical Drive E 2. Hard Drive C: 3. Embedded NIC | Port 1 | Partition 1 | Partition 1 : BRCM MBA Slot 0100 V15.2.10 Boot option Enable / Disable 1. Hard drive C 2.
Page 87
Chapter 5 - Servicing Serial communication Serial communication On without Console Redirection Serial Port Address Serial Device 1 = COM1 Serial Device 2 = COM2 External Serial Connector Serial Device 1 Fail Safe Baud Rate 115200 Remote Terminal Type VT100/VT220 Redirection After Boot Enabled System profile settings...
Network Speed 100 Mbps Duplex Mode Full Duplex 5.9.7 BIOS settings for Tab 51155517-600 System information Product name Dell PowerEdge T320 server System model name T320, 001 BIOS Version 2.0.22 or later System manufacturer Dell System Manufacturer Contact info www.dell.com...
Page 89
Chapter 5 - Servicing Memory information System memory size System memory type ECC DDR3 System memory speed 1600 MHz or greater System memory voltage 1.35 V Video memory 16 MB System memory testing Disabled Memory operating mode Advanced ECC Mode Node interleaving Disabled CPU information...
Page 90
Chapter 5 - Servicing Processor 1 Family – Model – Stepping 06-3E-4 Brand Intel® Xeon® CPU E5 [email protected] Level 2 Cache 6 X 256 KB Level 3 Cache 15 MB Number of cores SATA settings Embedded SATA ATA Mode or AHCI Mode ATTENTION During the Init Media installation, if the installation is unresponsive, change...
Page 91
Chapter 5 - Servicing 1. Embedded SATA Port Optical Drive E 2. Hard Drive C: 3. Embedded NIC | Port 1 | Partition 1 | Partition 1 : BRCM MBA Slot 0100 V15.2.10 Boot option Enable / Disable 1. Hard drive C 2.
Page 92
Chapter 5 - Servicing Slot Displacement Slot 1 Enabled Slot 2 Enabled Slot 3 Enabled Slot 4 Enabled Slot 5 Enabled Slot 6 Enabled Serial communication Serial communication On without Console Redirection Serial Port Address Serial Device 1 = COM1 Serial Device 2 = COM2 External Serial Connector Serial Device 1...
Page 93
Chapter 5 - Servicing System security Intel AES-NI Enabled System Password Not Enabled Setup Password Not Enabled Password Status Unlocked TPM Security TPM Activation No Change TPM Status Unknown TPM Clear Intel TXT Power Button Enabled NMI Button Disable AC Power Recovery AC Power Recovery Delay Immediate User defined delay(60s to 240s)
To exit the BIOS settings 1. In System Setup choose File > Save changes and exit. A confirmation message appears. 2. Click Yes. 5.10 Spare parts Dell part Honeywell Item Description number part number Processor Intel Xeon E5-2430 2.20 GHz , 7.2GT/s Intel 319-1186 51155517- Intel Xeon E5-2403 1.80 GHz, 10M Cache,...
5.11 Troubleshooting 5.11.1 Integrated Dell Remote Access Controller 6 (iDRAC6) issue Refer to the PN2014-13 for further information about iDRAC6 issue. You must search for the PN2014- 13 at the following Honeywell Process Solutions support website. http://www.honeywellprocess.com/support - 95 -...
Page 96
Documentation feedback You can find the most up-to-date documents on the Honeywell Process Solutions support website at: http://www.honeywellprocess.com/support If you have comments about Honeywell Process Solutions documentation, send your feedback to: [email protected]...
Page 97
For support, contact your local Honeywell Process Solutions Customer Contact Center (CCC). To find your local CCC visit the website, https://www.honeywellprocess.com/en-US/contact-us/customer- support-contacts/Pages/default.aspx. Training classes Honeywell holds technical training classes that are taught by process control systems experts. For more information about these classes, contact your Honeywell representative, or see http://www.automationcollege.com. - 97 -...